Input/Output limitations in Xenta 700 series controllers.

Issue

tam32 Error: "Max limit if number of in- and outlets is reached, this application cannot be generated."

Environment

Xenta 7xx

Xenta 700 series programmable controller.

Cause

Too many inputs and/or outputs in a Menta Object will cause generation to fail. 

Resolution

Reduce the amount of inputs or outputs in the program to < 500 total. This can be accomplished by splitting the faulty program into multiple Menta Objects (programs) in the controller.