Instances 29 and 30 of the Logic Block objects did not function correctly in an MN550 controller

Issue

Logic Blocks: Instances 29 & 30 of the Logic Block objects, 8-input AND/OR/NOR/NAND, did not function correctly in an MN550 controller. Instance 29 was always OFF and instance 30 was always ON (even with no inputs connected).

Environment

MN550

Cause

Firmware update is required.

Resolution

This has been corrected with MicroNet 50 controller Firmware version 5 released August 2008.

Additional information on firmware 5 can be found in TPA-LOND-08-0014.00