Issue

Integrating a SE7200F5045E to Niagara G3 / AX. The tenant can change the occupied heating or cooling setpoint locally.  Which snvt can be used to display the current setpoint?

Environment

Niagara G3

Niagara R2

SE7200 series

Cause

Application question - wants to plot the proper setpoint on the graphic

Resolution

The nciSetpts snvt displays the current setpoints used by the SE7200 for heating and cooling in both occupied and unoccupied modes.

Note:  The tenant can only change the occupied heating and cooling setpoints from the local keypad / display.