Invalid address in Vista when using non-Latin characters or space in the name of a signal in Device Editor.

Issue

If a signal name or description in XBuilder Device Editor has non-Latin characters (like Swedish å, ä, ö, Å, Ä, Ö) it will read [Invalid Address] when viewing the signal in Vista. Value pages are displayed correctly.

Environment

  • Vista version 5.1.5 or prior
  • Menta
  • Xenta
  • XBuilder

Cause

Signal name or description in XBuilder Device Editor has non-Latin characters (like Swedish å, ä, ö, Å, Ä, Ö) 

Resolution

Don't use non-Latin characters (Or space) for signal name or description.

This issue was confirmed in versions 5.1.2 - 5.1.5. It has been fixed in version 5.1.6.