Is it possible to get the temperature input from TAC Xenta 120 space temperature sensor damped?

Issue

The temperature readings from the space temperature sensor on the TAC Xenta 120 device is not stable, is it possible to damp the readings?

Environment

TAC Xenta 121-FC

TAC Xenta 121-HP

Cause

In some application, it is not possible to get a stable reading from the temperature sensor.

Resolution

It is possible to activate a filter for the space temperature readings.

Set the nciNodeAppOp2.bit14 to 1, this could be done from TAC Vista or from LonMaker. please note that the first bit is bit zero.

This will make the device to use 80% of the old value and 20% of the new reading.