Is it possible to use the analog output on the TAC Xenta 121-FC even if I want to have the Occupancy mode indicator on a STR150?

Issue

When using STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC, which is the only analog output on the TAC Xenta 121-FC device.

Environment

TAC Xenta 121-FC
STR150

Cause

When using a STR150 connected to a TAC Xenta 121-FC, the Occupancy Mode indicator will be default allocated to the Y1 output on the TAC Xenta 121-FC device, which is the only analog output on the TAC Xenta 121-FC device.

Resolution

In ZBuilder, it is possible to move the Occupancy Mode indication from the default location at Y1 to K1-4.

In this case you also need to have an external power supply with 5 Volt DC for the Occupancy Mode indicator.