Is the Continuum Cyberstation a B-OWS (BACnet Operator Workstation)?

Issue

Is the Continuum Cyberstation a B-OWS (BACnet Operator Workstation)?

Environment

Continuum Cyberstation

BACnet

Cause

Can't find reference to Continuum Cyberstation being defined as a B-OWS.

Resolution

The Cyberstation is a B-OWS and complies with ANSI/ASHRAE standard 135-2004. It just seems that it has not been BTL tested as I do not see it listed on their website or ours.

The following selection is taken from this document describing Continuum's Cyberstation capabilities.

"Native BACnet B-OWS
CyberStation communicates with the BACnet devices using BACnet/IP in strict accordance with ANSI/ASHRAE standard 135-2004 and is designed to function as a BACnet Operator Workstation (B-OWS) and BACnet Broadcast Management Device (BBMD). The CyberStation can communicate to all Andover Continuum BACnet Devices as well as any third party BACnet Device on the BACnet network."