Is there an X Driver available for BACnet MS/TP?

Issue

Can a Netcontroller II be used to communicate directly to BACnet MS/TP devices?

Environment

BACnet MS/TP RS-485 XDriver

Netcontroller 2, NC2

bCX9640

Cause

No X Driver is listed for BACnet MS/TP.

Resolution

There is no X Driver available for the BACnet MS/TP protocol to allow a NC2 to communicate to 3rd party MS/TP devices.

However a bCX1 4040 can directly communicate to BACnet MS/TP on its Comm2 and is BTL listed to confirm compatibility.

Also a bCX1 9640 can be converted to a 4040 by flashing it with the 4040 flash file available on the Extranet.