JACE-645-R2: The changing of the time zone in G3 Platform Administration is not being reflected in the R2 station?

Issue

JACE-645-R2: The changing of the time zone in G3 Platform Administration is not being reflected in the R2 station?

Environment

I/A series G3 JACE-645 R2

Cause

The time zone is not getting changed in the time.properties file for the JACE. 

Resolution

Manually set the Time Zone in the time.properties file as described below. 

1. In the G3 platform select File Transfer Client and on the right side go to /niagara/niagaraR2/sys to view the time.properties file.

2. Highlight the time.properties file and using the left arrow transfer it to the pc. 

3. Using a text editor like Notepad open this file, manually type in the desired time zone and save the change. 

4. Use the G3 Platform - File Transfer Client to transfer the altered time.properties file from the pc to the JACE and reboot the JACE. 

5. Open the station with R2 and confirm the time zone has been altered as desired.