Known issue: COV and Effective Occupancy

Issue

When an SE7000/SE8000 Series Room Controllers are bound to the MPM via ZigBee, "Effective Occupancy" does not follow "Occupancy Command" if the COV box is checked.

Environment

SmartStruxure Lite Multi-Purpose Manager

SE8xxx Room controller
SE8000 Series
SER8300, SE8300, SE8350, SE8600

SE7xxx Room controller
SE7000 Series
SER7300, SE7200, SE7300, SE7350, SE7600

Cause

Data type mismatch

Resolution

Uncheck the COV box for Effective Occupancy