Issue

Need to write a setpoint value from one controller to the setpoint of a different controller but the receiving controller does not show up in the Link Builder Client list.

Environment

I/A Series Workplace Tech Commissioning Tool - Link Builder

Cause

Only controllers that contain AVCOV or BVCOV objects will show up on the Link Builder "Client" side. 

Resolution

Link Builder "Server" objects can only link to AVCOV or BVCOV objects in a "Client" controller.  Once an AVCOV or BVCOV object is created in a controller that controller will show up in the "Client" list.  A setpoint value from a "Server" controller can then be linked to a AVCOV object of a client controller and used as desired in the client controller.