Issue

  • Links in TGML graphics in Webstation do not work.
  • A page can not be opened error message is shown. 
  • No Java is installed, TGML viewer mode in Websettings is set to Autodetect and "Optimized TGML loading" is set to On.

Environment

  • Vista Webstation 5.1.6
  • TGML Graphics

Cause

For some reason the links do not work when no Java is installed, TGML viewer mode in Websettings is set to Autodetect and "Optimized TGML loading" is set to On.

Resolution

In Vista Websettings change "Optimized TGML loading" to Off.