Issue

When creating Modbus RTU X Driver points any alarms attached to them or logging set up do not operate at all.

Environment

Modbus RTU X Driver

All  XDriver enabled controllers

Cause

The Modbus RTU X Driver is a Poll on demand X Driver which means it is not within the normal Controller Scan process, so alarms and logging will not update.

Resolution

As these points are outside of the controller Object Management System (OMS) these functions do not update.

Built into the X Driver is the capability to put an Annex point in the parameter 6 that will be updated along with the X Driver point, these annex points can then be alarmed or have logging attached as they are within the OMS and the controller scan process.