Longtext number is seen when a DI Object is displayed in System Manager and the object does not have an alarm.

Issue

A Longtext number is seen when a DI Object is displayed in System Manager when an Alarm is not configured on the object 

Environment

Sigma

Cause

A Longtext number is seen when a DI Object is displayed in System Manager when an Alarm is not configured on the object.

This does not occur with AI objects.

Resolution

An alarm on the DI object with Longtext may have been configured in the past and assigned with a Longtext number.

To prevent the Longtext from being displayed:

1. Re-enable the alarm, set the Longtext number on the alarm tab to "0"

2. Disable the alarm

3. Download the Object to the controller.