Issue

Choosing the correct range of sensor is important in order to provide the most accurate value.

Environment

SPD310

SPD360

Cause

Only the max value is specified for each range. How low is the lowest accurate value?

Resolution

The reasonable minimum pressure in the 100Pa range should be equal or greater than 40Pa (typically), otherwise the max. error becomes bigger.