Issue

Converting the entries from an MPX conrtoller error log can be useful when there has been a software revision change

Environment

EBO

MPX

Cause

There may be an entry in an MPX error log that shows as follows:

25           I               2018-07-02 10:07:36.56 0x00006409         0x20000015         0x80018a15         0x10000134         0x18061101          Software revision change

Resolution

The ability to extract the firmware revision numbers from the controller error log is useful especially if you do not have the device report.

Tale a look at the last 2 numbers of the following line:

25           I               2018-07-02 10:07:36.56 0x00006409         0x20000015         0x80018a15         0x10000134         0x18061101        Software revision change

0x10000134  == 1.00.01.00134  (please disregard the missing 01)

0x18061101 == 2018 06 11 (ignore the trailing 01 in the hex number)