MR-VAV-AX output 3 set to an AO instead of a DO

Issue

MR-VAV-AX output 3 set to an AO instead of a DO

Environment

MR-VAV-AX

Cause

This is correct. The output will always be labeled as an AO even thought the function of the output will be a DO

Resolution

If a DO is required for additional programming needs, create an internal DO point and use either a calculation or event sequence to control the new internal point.