MSTP Network reliability issue after creation via imported XML file.

Issue

After creating the MSTP network from an imported XML file, all devices under the network are offline and the network is unreliable.

Environment

BACnet

Cause

The MSTP network number is not included in the XML and must be reset manually.

Resolution

In the MSTP network property window set the Network ID to the appropriate number.

NOTE:

To bring the devices online see the following Lessons Learned article.