Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

MSTP Status object causes Device Learn failure at the UNC

Issue

Added the MSTP Status object to the MNB-1000 database and connected a constant tag to its network input and tested it with WorkPlace Tech and it functions as expected.  However, when doing a Device Learn of this MNB-1000 at the UNC it fails. 

The messages is "Learn Device Failed. ObjectId [binary_value:589834]".   The instance number after the binary_value may be different depending on other status objects in the database.

Environment

I/A Series Niagara R2

Cause

Cause is being investigated. 

Resolution

Use the Device Status object instead.  It will perform the same function and can be learned at the UNC without issue.

Tags (1)
Labels (1)
Version history
Revision #:
1 of 1
Last update:
2 weeks ago
Updated by: