Issue

Meter Points, Pulse Points Frequency, Pulse Point Width.

UNC496, UNC596, UNC696, UNC796 Pulse Point Location.

Environment

BAS, Sigma, 532, 632, x96

Cause

What is the maximum pulse repetition rate and minimum pulse width of a pulse/meter point configured on a digital input.

On a x96 controller, where can pulse points be configured.

Resolution

UNC532 - channels 1-2 object no's 81 - 82  repetition rate = 10 Hz , minimum pulse width of 50 milliseconds. Note if channels 3-10 object no's 83 - 90 are configured as pulse objects then the repetition rate = 0.5 Hz

UNC632 - channels 1-10 object no's 81 - 90  repetition rate = 10 Hz , minimum pulse width of 50 milliseconds.

UNCx96 (fitted with S-UNC-DI) - channels 1-16 object no's 81 - 96  repetition rate = 10 Hz , minimum pulse width of 50 milliseconds.

Note: For x96 controllers, pulse objects can only be configured in slot 6 of the controller.