Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Modbus TCP Device (Slave) address greater than 247

Issue

Modbus TCP Device (Slave) address greater than 247

Environment

Modbus TCP Network Gateway

Cause

Modbus TCP Device (Slave) address 248 is reserved and cannot be used. (Modbus TCP Network or Gateway)

SmartStruxure supports up to address 247, as the StruxureWare Building Operation - Technical Reference Guide

(up to v1.6.1)

Resolution

There was however a defect within v1.5.0 and earlier that caused address 250 to be used if the Device address is set to "Invalid"

This defect was corrected in v1.6.1

Address 255 is used as the Default address

Note
From v1.9 it is possible to define addresses for Modbus TCP devices from 1-247 and 249-255. Device addresses 0 and 248 are reserved.