Modifying the bypass occupancy override duration of a Xenta 102-AX

Issue

Modifying the bypass occupancy override duration of a Xenta 102-AX

Environment

Xenta 102-AX

LNS

Cause

There are several locations to change the bypass occupancy override duration on a Xenta 102-AX.

Resolution

To edit the bypass occupancy override duration from the Xenta 102-AX Plug-In:

  1. Open the Xenta 102-AX Plug-In
  2. Go to the Operating Parameters tab
  3. Alter the value under Bypass Override Duration (Hour, Min)

 

To edit the bypass occupancy override duration from an LNS Browser:

  1. Open the LNS Browser
  2. The value is represented in the format (days, hours, minutes, seconds, milliseconds).  If it reads (0,2,0,0,0) that would be an override duration of 2 hours.
  3. Alter the hours and minutes to the desired value, but leave the days, seconds, and milliseconds at 0.

 

To edit the bypass occupancy override duration from the Vista Workstation:

  1. Navigate to the Xenta 102-AX in the tree structure.
  2. Open the VAV_Controller module.
  3. Double click the point named UCPTovrdDuration
  4. The description breaks out separate values for days, hours, minutes, seconds, and milliseconds.  Alter the hours and minutes to the desired value, but leave the days, seconds, and milliseconds at 0.