Issue

Muster Report triggered to generate and print

Environment

Muster Reports on a Continuum site

Cause

With Muster Report loaded, can you trigger from a input (example: fire alarm) for a report to be generated and automatically print?

Resolution

With some workstation PE programming, you can launch the Muster Report to automatically print. You will need to install and configure the "Plain English Alarm Function" available from Lessons Learned 7658

This will trigger a workstation Function each time an alarm is received. You will write PE code to detect the specific alarm and/or point, then "Shell" to launch the Muster Report.

Please find the attached Muster Report User Guide and .dmp file which is renamed as .txt file which should be useful.