Niagara R2 GxText to indicate override (change color magenta) when linked object is in an override condition.

Issue

Niagara R2 GxText to indicate override (change color magenta) when linked object is in an override condition.

Environment

Niagara R2

Cause

Application

Resolution

There are various objects in the programLib jar that can be used to detect and indicate when an object is in an override condition. The hvac folder contains the AoCheckForOverride and BoCheckForOverride objects. These can be used to detect an override condition and set a boolean flag if an override condition exists.

The programLib util folder contains the ColorOvBinary and ColorOvFloat objects. Connect the priority input to the object being overridden and the object will change color when an override condition exists. In addition, the Active Text can be modified as required and connected to a GxText on a graphic.  The linked GxText will change color when the override occurs.