No alarm be triggered when the door is opening for a long time.

Issue

When configure a door with both reader channels as 0, only want to monitor the status of door switch, when the door is opening for a long time, the door ajar alarm should be triggered if the alarm has been configured, but on this condition, the door ajar alarm will never be triggered.

Environment

Cyberstation

ACX

AC-1

Cause

Maybe it is a design, the controller not consider is a door when the reader channel is 0

Resolution

Set a valid channel number for EntryReader although it is not connected, then try again, that should be OK.