No door transactions coming into AMT

Issue

No door transactions coming into AMT

Transactions are not been sent by only one door.

RX and TX lights on DPU / SCU are not flashing as per other DPU's  

Environment

I/NET

SCU / DPU

Cause

If you have the AMT masking set correctly and the Door Editor has transaction defined for the reader entry or exit and there are no transaction messages showing up in AMT. Then one of the issues might be the Quick Poll (QP) is turned off for that DPU. 

Resolution

The steps to correct this issue are detailed here: Quick Poll is not selected.doc