Not possible to bind a point in a Function block program to the RelinquishDefault property of a BACnet Multistate value in a SE8000 controller

Issue

It is not possible to bind a point in a Function block program to the RelinquishDefault property of a BACnet Multistate value in a SE8000 controller.

 

Environment

StruxureWare Building Operation(SBO) 1.6.1
SE-8000 series Room controller

Cause

In some circumstances the user may wish to change the value from both the HMI in SE8000 and from a Function block program in SBO, and in this case the RelinquishDefault property must be used.

Resolution

A possible workaround is to use a LUA script in the SE8000 controller.
 
Idea 1:
Write a LUA script that will check if the Priority array (ex. priority 16) value has changed for the list of points that the user wants to modify. If there is an entry in the Priority array, have the LUA script copy that value to Relinquish_default, then relinquish the corresponding priority array entry.
 
Idea 2:
There are 6 LUA "scratchpad" BACnet AVs that the user can write too. When the LUA script sees a change in those AVs, it can copy the value to a specific AV's relinquish default. For example scratchpad AV25 can be used to "shadow" a setpoint. So when AV25 changes, the LUA script will copy the present value of AV25 into the Relinquish_default of whatever the Setpoint's AV is.

Example of the LUA script in the SE8000 controller for the above:
If value AV25 is bigger than 0 the value of AV25 is written on AV39 Relinquish_default property(priority17) and then AV25 is set to 0 

 if ME.AV25 > 0 then ME.AV39_Present_Value[17] = (ME.AV25/10); end ME.AV25 = 0