Issue

When trying to add a point to a Group or graphic using the object browser in the object editor Continuum says the object is not available. 

When an occupancy point is added to the configuration page of a Continuum schedule and  the change is applied and the editor closed, upon re-editing the schedule the point is no longer attached.

Environment

  • Continuum
  • CyberStation
  • Object Editor
  • Browse

Cause

An object name violation has occurred.

Resolution

Check for objects that have been given the same name as the Continuum Network under which the controller resides in the object tree. 

Once a Continuum Network is given a name the name should not be used for any other object in the database.