Objects don't work properly or indicate fault when created in a b3 controller.

Issue

Go to templates folder

Drag Event Enrollment to controller to create a new event enrollment

It prompts for event notification and point reference and enrollment looks fine.

When alarm is tested the event notification does not work and indicates fault.

Environment

Continuum

BCX40xx

B3

B4920

Cause

A Send to Database was not performed on the controller in the BACnet side of the Continuum Object Tree.

Resolution

When objects are added or modified on the Infinity side of Continuum's Object Tree, the changes do not take affect in the controller until a Send to Database is performed on the controller from the BACnet portion of Continuum Explorer Object Tree.