On a SE7600 controller, is the nciSccModel snvt read-only or will it modify the controller's profile?

Issue

On a SE7600 controller, is the nciSccModel snvt read-only or will it modify the controller's profile?  Customer has replaced the HVAC equipment such that the existing profile does not match up with the existing SE7600.

Environment

SE7600

VT7600

Cause

Mechanical equipment was replaced with a different design

Resolution

The nciSccModel snvt does not modify the SE7600 profile.  It is a read-only.

A different model of controller is the best option for the new mechanical design.

An external solution may also work (i.e. the use of a relay).