One of the properties for the LON object in the 511 is 'Use subnet node addressing' what does this do?

Issue

One of the properties for the LON object in the 511 is 'Use subnet node addressing' what does this do?

Environment

  • Xenta 511 LTA
  • LON Network

Cause

If you import a LNS network into XBuilder and are going to use polled values from a LonWorks devices, you can choose if the Xenta 511 is going to use subnet/node or neuron ID to address the current LonWorks devices.

Resolution

The advantage to using subnet/node addressing is that importing the LNS network into XBuilder again if node is replaced in the LNS network is not necessary, provided that the node keeps the same subnet/node and the same application.

 