Open time schedule in OGC graphic from Webstation.

Issue

Is it possible to open a time schedule from a OGC graphic when the graphic is opened from Webstation?

Environment

TAC Vista 5.1.x 

Cause

In older versions of TAC Vista a "Command Point" object could be used to link to a time schedule and it worked fine in booth Webstation and Workstation.  And that still works fine in Workstation but to get it to work in later versions(5.1.x) a "Dynamic Value" object must be used in the graphic editor to get it to work in Webstation.

Resolution

Use a "Dynamic value" object in the OGC editor when linking to a time schedule to get it to work in TAC Webstation.