Issue

Can't  Override/force an I/O point on an I/O-Module connected to a Xenta 7xx

Environment

Vista
Xenta 7xx

Cause

Xenta 7xx way of override value has been changed from the way Xenta 4xx did

Resolution

There are no way of forcing the RI/BI or RO/BO signals like you can do with the AI/AO DI/DO in Xenta 300/400/280. In the 700 you can only force the real physical point. You find the points under the Xenta Server object $IO.