Issue

Desire to create a Panel in the BACnet Application folder

Environment

StruxureWare Building Operation 1.0 and higher

Cause

Desire to create a panel in a subfolder, such as BACnet Application folder.

Resolution

Panel(s) and inability for creation in the BACnet Application folder is intentional.

The BACnet Application is mostly reserved objects which are visible to BACnet (Points, Values, Alarms, Trends, Schedules, etc), and also non-BACnet objects that you might use with BACnet objects (Graphics, Extended Trend Logs, Charts and Lists). Things that are application like…

The Panel object is really related to the Workstation and its layout, not really corresponding to the application-like objects that are available in the BACnet application. I think you can observe that the Panel objects can also not be created inside of any other communication protocol interfaces. For example, under a LonWorks, or ModBus, you also cannot create Panel objects…
 