Phoenix Integration to Continuum

Issue

Trying to discover Bacnet IP but only some of the devices are brought in.

Environment

  • Phoenix Virtual Server
  • Continuum 1.9X

Cause

Two BBMDs configured on the same Subnet

Resolution

 Only One BBMD per Broadcast domain / Network is required in a BACnet Network

  1. Web over to the BCX and disable the BBMD function 
  2. Do a network teach 
  3. Delete the Phoenix Network from the Bacnet side in Continuum
  4. Do a Find New Bacnet  from the Continuum Root.