Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

ProView for LON configuration wizard for I/A Series G3 will not expand and display the nvi, nvo, and nci objects for the MNL-800 controller

Issue

During the menu configuration process, the ProView for LON configuration wizard will provide a list of LON devices commissioned into the G3 station database.  The MNL-800 controller appears in the list, however,  the MNL-800 device object cannot be expanded to display the nvi, nvo, and nci objects for selection.

Environment

I/A Series G3 (all versions), MNL-800, ProView for LON, MNL-PROV-WAL

Cause

None

Resolution

The MNL-800 will not display network variable nvi, nvo, and nci objects unless the device's self documentation is modified to provide what the wizard considers a valid LonMark and function block reference.

  1. Open the properties for the MNL-800 (Dynamic Device) and expand the Device Data. Locate the Self Doc property and configure the value as follows: 3.3@8000;
  2. Launch the Ec Dis Wizard and the MNL-800 will now expand to display the nvi, nvo, and nci objects for selection.
Tags (1)
Labels (1)
Version history
Revision #:
1 of 1
Last update:
‎2018-09-06 01:53 PM
Updated by: