Procedure for replacing a Continuum BCX 4040 controller

Issue

Procedure for replacing a Continuum BCX 4040 controller

Environment

Continuum Cyberstation

BCX 4040

Cause

Verification of steps to replace a BCX 4040

Resolution

  1. Commission new BCX through webpage configuration same as old BCX except Bacnet Configurable Properties section.
  2. Bacnet Configurable Properties - Bacnet Device ID = The same ID in the old BCX (by default serial number)
  3. Bacnet Configurable Properties - Bacnet Port Number UDP = Same as old BCX (BAC0 by default)
  4. Bacnet Configurable Properties - Bacnet Network ID UDP = Same as old BCX (1 by default)
  5. Bacnet Configurable Properties - Bacnet Network ID Comm2 = Same as old BCX (2765 by default)
  6. Bacnet Configurable Properties - Bacnet Mac ID Comm2 = Same as old BCX (0 by default)
  7. Bacnet Configurable Properties - Bacnet MS/TP Enhanced Mode = Same as old BCX (TRUE by default)
  8. Bacnet Configurable Properties - Bacnet BBMD Enabled = Same as old BCX (False by default)
  9. With BCX online in Continuum Explorer, select menu item Options\Send to Controller options
  10. Select Reload attached objects, but not attached controllers - select ok
  11. Verify the BCX Comm2 settings and baud rate speeds.
  12. In the Continuum Explorer, right click on the BCX and perform a send to controller.
  13. Verify points and communications.