Issue

A program is entered in a point's alarm configuration but the program does not run when the point goes into alarm.

Environment

CyberStation

All CXs

All i2 and b3 devices

Cause

Event notification object not configured to run program.

Resolution

In the Event Notification's actions list, select the 'Run Program' action.