Programmable Points using the + add function to totalise alarms e.g. POINT 0|14 ALARM + POINT 0|15 ALARM

Issue

Programmable Points using the + add function to totalise alarms

Alarm Integrator

10 XFlo = POINT 0|14 ALARM + POINT 0|15 ALARM + POINT 0|16 ALARM
20 YFlo = POINT 0|17 ALARM + POINT 0|18 ALARM + POINT 0|19 ALARM
30 RETURN VIA TEXT 91 VALUE XFlo + YFlo

Environment

BAS

Sigma

B2S Upgrade

Alarm Integrator

Cause

The following point was used in BAS to calculate the number of alarms.

10 XFlo = POINT 0|14 ALARM + POINT 0|15 ALARM + POINT 0|16 ALARM
20 YFlo = POINT 0|17 ALARM + POINT 0|18 ALARM + POINT 0|19 ALARM
30 RETURN VIA TEXT 91 VALUE XFlo + YFlo

Resolution

The point compiles and runs in the prog point editor however the point in does not work in the Sigma controller.  

The programmable point will require re-writing.

Depending upon the number of alarm points that were originally monitored, more than 1 point may require writing as there will be insufficient tokens.

10 XFLO = 0.0
20 IF POINT 0|14 ALARM THEN XFLO=XFLO+1.0
30 IF POINT 0|15 ALARM THEN XFLO=XFLO+1.0
40 IF POINT 0|16 ALARM THEN XFLO=XFLO+1.0
50 IF POINT 0|17 ALARM THEN XFLO=XFLO+1.0
60 IF POINT 0|18 ALARM THEN XFLO=XFLO+1.0
70 IF POINT 0|19 ALARM THEN XFLO=XFLO+1.0
80 RETURN VIA TEXT 91 VALUE XFLO

If more than 1 point is required to be written, then the final point required to combine all the alarm totals and is written as follows:

10 XFLO=(POINT 0|a + POINT 0|b + ......)
20 RETURN VIA TEXT 91 VALUE XFLO