Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.


Issue

Orphan alarm exists in the Enterprise Server database and acknowledgement of the alarm does not remove the alarm.

Environment

StruxureWare Building Operation site with ES

Enterprise Server, PersistedData.dat 

Cause

Backup of the SmartStruxure Building Operation database that includes Historical data will include the alarm that needs to be purged. Ip changes or other reasons can contribute to alarms being orphaned.

Resolution

In order to completely purge an alarm database it is necessary to delete the PersistedData.dat file that stores this information in the database.

1. Perform and ES and AS full backups

2.  Using Building Operation Software Administrator click the "Stop Service" button for the Enterprise Server.

Image from Windows XP

Image from Windows 7 / 10

3. Browse to the database path listed in the Building Operation Software Administrator tool.

Windows 7/10:       C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\db

Windows 7/10:       C:\ProgramData\Schneider Electric StruxureWare\Building Operation 2.x\Enterprise Server\db

Windows XP:       C:\Documents and Settings\All Users\Application Data\Schneider Electric StruxureWare\Building Operation 1.X\Enterprise Server\db

4. Browse to the Persistent subdirectory

5. Move/Delete the PersistedData.dat  file

6. Click the "Start Service" button in the Building Operation Software Administrator tool.

When the Enterprise Server restarts and you login the orphaned events will be removed and any currently present alarms will return to the Alarm window with their proper status and assignment. This process causes a re-evaluation of alarms on the ES and fetches all the alarms from each AS. This can take a few minutes and may cause some slowness in the system.