Issue

RM3601 / XRM3201 Wiring connection details.

Environment

RM3601

3601

XRM3201

3201

Actuators

Wiring

connection details

Cause

Actuator wiring details.

Resolution

The RM3601 actuator is a 230 volt actuator, its connection details are as follows;

Terminal 1 - Connection for open signal (230V live)

Terminal 2 - Connection for close signal. (230V live)

Terminal 3 - Connection for Neutral.

Terminal 1T - Transfer connection, passes 230V to other devices when actuator is open.

Terminal 2T - Transfer connection, passes 230V to other devices when actuator is closed.

The XRM3201 actuator is a 24 volt actuator, its connection details are as follows;

Terminal 1 - Connection for open signal (24 volts)

Terminal 2 - Connection for close signal. (24 volts)

Terminal 3 - Connection for zero volt.

Terminal 1T - Transfer connection, passes 24V to other devices when actuator is open.

Terminal 2T - Transfer connection, passes 24V to other devices when actuator is closed.