Replacement of Satchwell "M 1301" Actuator forming part of combined Actuator / 3-port Valve Body assembly due to obsolescence.

Issue

Satchwell "M 1301" Actuator forming part of combined Actuator / 3-port Valve Body assembly requires replacement.

Environment

  • Stand alone Satchwell “M 1301” Actuator forming part of combined Actuator / 3-port Valve Body assembly
  • M 1301
  • Actuator
  • 3-port
  • Valve Body

Cause

Obsolescence of Satchwell "M 1301" forming part of combined Actuator / 3-port Valve Body assembly.

Resolution

There is no direct replacement for the "M 1301" Actuator and as a result both the "M 1301" Actuator and the 3-port Valve Body to which it is connected will also require replacement. 

Replace Satchwell “M 1301” combined Actuator & 3-port Valve Body assembly with Schneider Electric MD10B-230 Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size.

Details of the original Satchwell “M 1301” combined Actuator & 3-port Valve Body assembly may be viewed here.

Details of the replacement Schneider Electric MD10B-230 Actuator may be viewed here.

Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here.

Details of the replacement Satchwell MB 3-port Valve Body may be viewed here.

N.B.

It is possible that the "M 1301" Actuator may have been fitted with an Auxiliary Switch.

If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B-230 Actuator if required.

Details of the MD-S1 Auxiliary Switch may be viewed here.