SBO is not supporting enumerated values.

Issue

Binding to Security Expert values through EWS results in "Type does not exist" error when attempting to save a binding.

Environment

SmartStruxure

Security Expert

Cause

The value being bound was coming through and mistakenly being created by SBO as an enumerated value which is not supported. The value is actually an integer.

Resolution

A hotfix has been created to resolve this in SBO 1.9.1.6700.
 
There is also a workaround that works for previous versions of SBO.
 
If you update (configure) the value type of the EWS ValueItem property Value with the system.pt.Int32 it will work to do bindings.
 
1. Open the propertydialog of the EWS ValueItem and click the configuration button of the Value property. 


 
2. Check the Type checkbox which already contains the value type system.pt.Int32.
3. Press Ok and save the change in the dialogproperty.
4. Now it's ok to do bindings with this Value.