Issue

The ZigBee network configuration parameters (Channel and PAN ID) of the MPM matches those of the room controller, but the room controller will not come online.

 

Symptoms:

- For SE(R)8000 Series: The "ZigBee Short" field in the "Network" menu option keeps changing.

- For SE(R)7000 Series: The Green LED is blinking twice where 3 blinks are expected. (Description of LED status defined in Article #16434)

Environment

SmartStruxure Lite Multi-Purpose Manager

SE8xxx Room controller
SE8000 Series
SER8300, SE8300, SE8350
Viconics branding VT8000 Series

Cause

A temporary bug causes the MPM to prevent a specific ZigBee com module (installed inside the room controller) from joining the network on a particular channel.

Resolution

MPM has to be reset using one of the following methods

Method 1: Unplug and replug power to the MPM

Method 2: Click on the "Restart Controller" button as shown in image below. Note: Database must be saved before restarting the controller to avoid loss of data.

 

 restart-controller.jpg