SNVT_temp not showing the correct value in TAC Vista

Issue

Some SNVT_temp values are not showing the correct value in TAC Vista. They are always a couple of degrees off. The correct value is displaying in LonMaker.

Environment

  • SNVT_temp
  • Vista Workstation

Cause

This can be caused by the gain not being set to the right value in the properties for the object.

Resolution

The gain should be 0.018. The problem is that with default Windows settings, the gain is only shown with 2 decimals, so it will be presented as 0.02.

If you have changed the gain, you have to type in 0.018 even though it will be presented as 0.02.

If you want to see all the decimals you have to change the ‘number of digits after decimal’ to 3 in Windows regional and Language settings.

 