Issue

Configuring the SSC to use Comm Port B on an SSC.

Environment

AccessXpert

Server 2012

SQL 2012R2

Hosted Instance Version 2, Version 3

Premise Install

Cause

The SSC is not configured to work on Comm Port B for the RS-485 connections, all communications to downstream devices are done through Comm Port A. If you have done so and it functions, please note that this is not supported.

Resolution

All communications on an SSC for RS-485 in Accessxpert needs to be done on Comm Port A.