STR-150 Not Compatible With Software Version 1.1 Xenta 100 Series Controllers

Issue

  • The STR-150 Wall Module with Display is not compatible with Xenta 100 controllers that are earlier than SW-version 1.2.
  • The space temperature (nvoSpaceTemp) is displaying an invalid or default value (either 621.81 degrees Fahrenheit or 327.67 degrees Celsius). In newer versions of Vista the value will display "Invalid Value".

Environment

  • STR-150
  • Xenta 101-VF
  • Xenta 102-ES
  • Xenta 103-A
  • Xenta 104-A

Cause

Software for Xenta 100 series controllers previous to version 1.2 is not compatible the STR-150 wall module.

Resolution

The STR-150 is only compatible with Xenta 100 series controllers that are software version 1.2 or later.

If a wall module with display is required for a Xenta 100 controller with software that is older than version 1.2 there are two possible solutions:

  1. An identical Xenta controller can be purchased with the latest software version to replace the old controller.
  2. An STR-350 stat can be used and connected to the Xenta controller via SNVT bindings.