Knowledge Base
cancel
Showing results for 
Search instead for 
Did you mean: 

Schedule in the AS will not control value in a b3 controller.

Issue

An Enumerated schedule created under the BACnet Interface application folder will not control a digital value (Occupancy) in a b3 controller. 

Other b3 controllers are handling this with no trouble.

Environment

  • b3
  • Variable Connectors
  • Schedules
  • bindings

Cause

Broken variable connectors.

Resolution

  • Deleted the bindings and performed  a Repair References on variable connectors.
  • The digital value responded properly once the schedule binding was re-established.