Issue

Setpoint in OP can't be Changed to the Value above 100, while in Workstation it can be changed at any range.

Environment

Vista

OP

Cause

The default changing range of an analog value in OP is from 0 to 100. If the value needs to be changed beyond this range, the default property needs to be modified.

Resolution

Click Tool-OP Configuration in Menta to open the OP configuration window. Click on the value that needs to be changed, and choose property. Modify the minimum and maximum value of this value. Then this value can be changed in OP freely.