Setting up an Alarm Notification class separate from the default Notification Class 0.

Issue

Setting up an Alarm Notification class separate from the default Notification Class 0.

Environment

Niagara R2, Enterprise Server, UNC-410, UNC-520

Cause

Do not want to send all alarms to Email Recipient.

Resolution

- Setup a new Notification class and assign it to the alarms you want emailed.
- Link the output of the Notification class to the input of the MailRecipient.
- Go to the Alarm Setup tab of the objects you want emailed and set its notificationClass property to that of the Notification class you just added. .

Only the alarm associated with the added Notification Class will be emailed.
 